Hello,
I have a building that has (2) services (1) 120/240 and 240 volt delta. I was failed by the electrical inspector because I did not have (2) grounding electrodes installed into each enclosure? I installed a separate isolated ground bar in the electric room and I ran a GEC from the water pipe to a ground bar and I also ran a GEC to the ground rods to the ground bar and I also ran a grounding electrode conductor from the buidling steel the this ground bar.. Then I ran separate GEC to each service enclosure and termiated on the grounding bars. What is the violation here??
I have a building that has (2) services (1) 120/240 and 240 volt delta. I was failed by the electrical inspector because I did not have (2) grounding electrodes installed into each enclosure? I installed a separate isolated ground bar in the electric room and I ran a GEC from the water pipe to a ground bar and I also ran a GEC to the ground rods to the ground bar and I also ran a grounding electrode conductor from the buidling steel the this ground bar.. Then I ran separate GEC to each service enclosure and termiated on the grounding bars. What is the violation here??