EEC said:
Outdoor 450KW Generator with 1000A Breaker. Does the neutral need to be bonded to the grounding conductors at the generator? Or can the neutral be bonded inside building at the first service rated disconnect?
If this generator is the
sole or whole source it should be treated as a separately derived system because it would be the
only source. If this is the case you need to bond the neutral at either the generator or the first disconnect (which is the transfer switch). The grounding electrode conductor must connect at the same location. The bonding usually takes place at the transfer switch. Notice ?Separately Derived Systems? in definitions and 250.30.
If this is a second source to supply portions of distribution and the grounded ? neutral ? conductor does not open with the transfer switch it is
not a separately derived system (SDS) because the ground fault path remains available to either source in the event of a short. This is most common with multiple sources.
It?s all about the fault path back to source to allow extremely high current as fast as possible which enables overcurrent protection to function ? trip the breaker. Fault current is not trying to go to earth it is trying to return to its source.
Returning unused current does not follow the path of least resistance it follows ALL paths to its source, so it is important to control neutral current trying to return to its source solely on a conductor. If neutral bonding happens incorrectly or in multiple locations a parallel path of dangerous touch voltage will exist on conductive items other than the actual conductor. This is why the bond must take place at either the source or the first disconnect.
A transformer (if not an auto) is a SDS and the bonding usually happens at the transformer with the XO tap, if it is a grounded system, but not past the first disconnect or at both locations. If there is no XO tap like 480V 3W delta none of the three transformers are grounded it is simply 3 phases and this is considered an ?ungrounded system? for this reason. Not because there is no electrode, grounding electrode conductor, or equipment grounding these are all still required. A system is qualified as ?grounded? or ?ungrounded? only by the existence of one of its transformers connected to earth ? usually through the XO tap.