romex jockey
Senior Member
- Location
- Vermont
- Occupation
- electrician
210.8(A)(7) Sinks - where receptacles are installed within 1.S m
(6 ft) of the outside edge of the sink
Kitchen designed with range w/in 6' of sink.....
New 30" slide in gas range (major manufacturer) fed via afci/gfci combo brkr and wiring installed to the '14 trips on operation of unit
So.....does this qualify as a 110.3(B) >>>>>(copied from the manufacturers instructions)
Electrical Requlrements
120 volt, 60 Hertz, properly grounded dedicated circuit
protected by a 15 amp circuit breaker or time delay
fuse.
Note: Not recommended to be installed with a Ground
Fault lnterrupt (GFl).
Do not use an extension cord with this range.
~RJ~