GFCIs under kitchen sinks

Status
Not open for further replies.

DKK

New User
Location
Lubbock, TX
Electrical Engineer

Electrical Engineer

Garbage disposal and/or dishwasher possibly

The explanatory information included in NEC 2014, 210.8 (6) states "Receptacles installed for disposers, dishwashers, and trash compactors are not required to be protected by GFCI's".

210.8 (6) states where receptacles are installed to serve countertop surfaces.
210.8 (7) states where receptacles are installed within 1.8m (6ft) of the outside edge of the sink.
 

mwm1752

Senior Member
Location
Aspen, Colo
The explanatory information included in NEC 2014, 210.8 (6) states "Receptacles installed for disposers, dishwashers, and trash compactors are not required to be protected by GFCI's".

210.8 (6) states where receptacles are installed to serve countertop surfaces.
210.8 (7) states where receptacles are installed within 1.8m (6ft) of the outside edge of the sink.

You've stated code , commentary, whats you point?
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
The explanatory information included in NEC 2014, 210.8 (6) states "Receptacles installed for disposers, dishwashers, and trash compactors are not required to be protected by GFCI's".

210.8 (6) states where receptacles are installed to serve countertop surfaces.
210.8 (7) states where receptacles are installed within 1.8m (6ft) of the outside edge of the sink.

...and (6) is not driving the truck when you're having to GFCI protect a disposal, a dishwasher, or a trash compactor. 210.8(A)(7) is, because you can't hardly install a disposal or a dishwasher receptacle and not fall within 6' of the kitchen sink.

If the writers of the commentary did not pick up on the NEC requirement, boy, that sure is embarrassing for them! :)
 

jxofaltrds

Inspector Mike®
Location
Mike P. Columbus Ohio
Occupation
ESI, PI, RBO
The explanatory information included in NEC 2014, 210.8 (6) states "Receptacles installed for disposers, dishwashers, and trash compactors are not required to be protected by GFCI's".

210.8 (6) states where receptacles are installed to serve countertop surfaces.
210.8 (7) states where receptacles are installed within 1.8m (6ft) of the outside edge of the sink.

The commentary does NOT state that.

Read the "if" part.
 