(D) Bathtub and Shower Areas. No parts of cord connected
luminaires (fixtures), chain-, cable-, or cordsuspended-
luminaires (fixtures), lighting track, pendants, or
ceiling-suspended (paddle) fans shall be located within a
zone measured 900 mm (3 ft) horizontally and 2.5 m (8 ft)
vertically from the top of the bathtub rim or shower stall
threshold. This zone is all encompassing and includes the
zone directly over the tub or shower stall. Luminaires
(lighting fixtures) located in this zone shall be listed for
damp locations, or listed for wet locations where subject to
shower spray.
IE: If it is one of the luminaries listed it can't be in the all encompassing zone, if it is one that is allowed to be within the all encompassing zone then it must meet the last sentence of the requirement to be within that zone....atleast thats how I read it....so surface mounted luminare within the encompassing zone 3' x 8' would need to be damp location rated...
( 2005 NEC )
So. I should use "Rust-oleum" on the open can trim?