ceb58
Senior Member
- Location
- Raeford, NC
Had a call today to look at a hot switch box. Dont know the temp. but you could not leave your hand on it long. Here is the set up. 3 gang surface mounted metal box, each switch is a 20amp sp. Each switch controls 6- 8' 4 lamp fixtures. They are fed from a 20 amp 3 pole breaker, #12 thwn, MWBC in 3/4 emt. The neutral is ran from panel into switch box, then it runs with the switch legs to ceiling j-box where each run is separated. I clamped each one and they are pulling around 15.5 amps each. The switch box is getting very hot to the touch and owner is concerned about the heat. These lights are on 10-12 hrs. per day. The only thing I can think to do would be change the 3 gang to single gangs and stack them to prevent excess heat build up. Any other ideas?