210.11(B)(B) Load Evenly Proportioned Among Branch Circuits.
Where the load is calculated on the basis of volt-amperes
per square meter or per square foot, the wiring system up to
and including the branch-circuit panelboard(s) shall be provided
to serve not less than the calculated load. This load
shall be evenly proportioned among multioutlet branch circuits
within the panelboard(s). Branch-circuit overcurrent
devices and circuits shall be required to be installed only to
serve the connected load.
I don't see how you can interpret this the way you seem to be. iwire, Jumper, what exactly is your definition of "this load"? I dislike the ambiguity of 210 and 220. For the record, I couldn't find 210.11(B) when I was looking but it is what I was looking form. There is one other way you could look at it. By dividing the square footage by the number of circuits and trying to circuit such that each circuit covers a portion that way, regardless of the number of receptacles, but either way, the three dedicated in a hallway and everything else on one circuit scenario would not be allowed. I am open to a different interpretation, I just don't see it.