It is very doubtful that you would get 2 _separate_ 120/240V single phase services. In addition to other issues, such a setup violates code.
Could you explain that? As in, two services attached to one building violates code?
I haven't seen anything that prohibits having more than one meter on one property.
Your inverters are limited to 480/277V wye. Your choices are:
1 have the utility supply 480/277V, and then provide your own transformer to give 120/240V,
2 have the utility supply 208/120V, and then provide your own transformer to give 480/277V
3 have the utility supply 240/120V high leg delta, and then provide your own transformer to give 480/277V
All of the 480V to 208 or 240V transformers that you are looking at have _delta_ primaries. This means that each individual coil on the secondary side actually loads _two_ of the inverters on the primary side.
1 is too pricey and too complicated.
2 208 won't be used, so why not stay with 120/240 split/single phase?
3 i don't think they'll supply high leg- they supply 200A, 400A, and over 400A, which is this- Single-Phase, 3 Wire, 120/240V for
Loads 72 to 100kVA Demand or Three-Phase up to 800A From Overhead Line
So it could turn out that they don't mind all 75kVA/60kW of PV going into just one of the overhead lines, at either 120/240 OR 208/120.
Which I suppose simplifies things somewhat.
And that last 277 to 120/240 xfmr I posted was this-
Primary configuration | One Winding |
Secondary configuration | Two Winding |