inspector

Status
Not open for further replies.

desertplace

New member
Hi Mike, i am currently the sole inspector for a casino in upstate n.y. my ques. is on multiple circuits. before i approach the electrical contractor i need some guidance on art. 210.4 and following. it is my understanding that, these requirements need to be meet. even though the circuits here may not be on the same yoke, or strap. i have a hotel -casino in the hotel portion there is 22 rooms per floor all feed from a electrical room on each floor. they are fed with a #8 mc cable 3 hots 1 neutral. all on single pole breakers. it is my understanding that these need to be on a 3pole breaker.

Thanks in advance,
Bill
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
If these are truly multiwire circuits and not feeds to another panel then I see no need for them to be on a 3 pole breaker unless they terminate on the same yoke of a device. Would you want the entire area to go out when there is a short or overload on one phase? I don't think so--- Now the 3 single poles must each be on a separate phase otherwise you can overload the neutral.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I agree with Dennis. There is no requirement for these MWBC's to be on handle tied breakers.

Roger
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Take a look at ROP 2-10

Proposal 2-10 ? Will require common disconnect of all ungrounded conductors of all multi-wire branch circuits installed in all locations.

Here is the ROC for 2-10

Comment 2-10 ? The panel reversed itself on the requirement to identify each grounded conductor of a multi-wire branch circuit. The common disconnect and grouping of the conductors in the panelboard requirements remained.

I may be wrong but it seems to me the CMP has accepted the requirement for a common disconnect for all ungrounded conductors of a multi-wire branch circuit for the 2008 NEC.

Chris
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Hi Mike.

Chris, I'm still hoping it falls by the way side. :smile:

Roger
 

GeorgeB

ElectroHydraulics engineer (retired)
Location
Greenville SC
Occupation
Retired
raider1 said:
Proposal 2-10 ? Will require common disconnect of all ungrounded conductors of all multi-wire branch circuits installed in all locations.

I may be wrong but it seems to me the CMP has accepted the requirement for a common disconnect for all ungrounded conductors of a multi-wire branch circuit for the 2008 NEC.

Chris

The OP does not have MWBC ... each circuit is fed with one phase and one grounded conductor. If a 208 single phase circuit is involved, those (2) would be, and (on a single yoke) need handle tie common trip.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
ryan_618 said:
I don't think it will. I got a lot of support.

Darn! :D

I can still hope, even if it's for a miracle.

Roger
 

donselectric

Senior Member
Location
nh
if there is no line to line devices and they run all line to nuet
loads why would you need ties its not a muti wire circuit

jmo
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
donselectric said:
if there is no line to line devices and they run all line to nuet
loads why would you need ties its not a muti wire circuit

jmo

Line to neutral loads are what make up a MWBC

Branch Circuit, Multiwire. A branch circuit that consists of two or more ungrounded conductors that have a voltage between them, and a grounded conductor that has equal voltage between it and each ungrounded conductor of the circuit and that is connected to the neutral or grounded conductor of the system.

Roger
 

Shockedby277v

Senior Member
Location
Michigan
1010777385_2.gif
 

ryan_618

Senior Member
Shockedby277v said:
Why their not sharing neutrals in this picture is beyond me.
Because that graphic is showing "multiple circuits", which is what 210.7 addresses. If you look in 210.4, you will find a similiar graphic for multiwire branch circuits.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Shocked, as Ryan points out, there is a diffence between 210.4 and 210.7.

Roger
 