vermathrax
Member
- Location
- florida
I am a Meter Tech and I was doing a voltage check on a single phase 120/240 socket. I was getting 120v phase to ground and phase to neutral on both legs. I was only getting 6.5 volts phase to phase. I checked the house next door to the one I was working on and had good voltage on all tests.Both houses come from the same drop pole and the same transformer. Any ideas on what could cause this? I though at first it was an open neutral but that is not the case with me getting good readings phase to neutral. Any help would be greatly appreciated.
While I wont be the one going back to fix the job I would like to know just for my own knowledge. Thank you.