You need 144KVA. That's 400A*208*sqrt3.
If you are providing anything less than 144KVA you are not meeting the contract.
The breaker size and wire size is inconsequential to the argument other than it has to carry at least 400A, and be sized properly.
It's usually better to deal in KVA for load sizing.