if a laundy room is the exact size of the washer dryer and the power requirement is 30 amps 220volts is there still a requirement for a dedicated laundry receptical ??
480sparky said:Yes. 210.52(F).
Stickboy, I think that Code ref is a little off. 210.11(C)(2) makes no mention of a 120v circuit any more.
stickboy1375 said:Correct, that was a change from the 2002 to the 2005.
celtic said:"What if" the "laundry room" is no more than the width and depth of the combo washer/dryer ?
Imagine if you will, a closet sized area (with a bi-fold door) that allows ONLY for the W/D and nothing else....going a step further, this W/D location is in a hallway.
celtic said:"What if" the "laundry room" is no more than the width and depth of the combo washer/dryer ?
Imagine if you will, a closet sized area (with a bi-fold door) that allows ONLY for the W/D and nothing else....going a step further, this W/D location is in a hallway.
480sparky said:Actually, that code section has never mentioned voltage. It changed from 220-4 in the '99, but never mentions anything more than a 20-a circuit all the way back to when it was born in 1968. Back then, 220-4(h)(2) only required a 1500-watt 2-wire circuit.
stickboy1375 said:Pretty strange, why do you think it was even worded like that?
480sparky said:It's still required.
stickboy1375 said:Then you still need the 120v 20a circuit. There are no WHAT IF''s... it says what it says.
celtic said:Interesting....
A couple of years back when I did the condos, we had the exact scenario I described.
No laundry outlet was installed.
The EI was/is a very sharp guy.
I don't know why this was overlooked/allowed.
celtic said:Interesting....
A couple of years back when I did the condos, we had the exact scenario I described.
No laundry outlet was installed.
The EI was/is a very sharp guy.
I don't know why this was overlooked/allowed.
stickboy1375 said:I find it strange I am forced to install anything to do with laundry, seems like a luxury item to me... Never liked 210.52 anyhow.
480sparky said:So are coffee pots, mixers, bread makers, cappucino machines, popcorn poppers, malt mixers and mircowaves. You still happily install the two SABCs, don't you?
stickboy1375 said:Not happily, no.
480sparky said:Don't you get paid to do this?
480sparky said:210.11(2)(2) appears to only require a minimum of a 20-amp circuit. Maybe that's what the EIs take on it was. As long as there's a 30-amp, then that's all that was needed.
But 210.52(F) requires a 120v 20a.
stickboy1375 said:So am I supposed to still be happy?
Lcdrwalker said:Could this be a matter of semantics? What if the laundry equipment were in a utility are instead of a laundry room or maybe a closet?