I agree that since both motors are on the load side of the 255 amp MDP main then the 60 hp motor is fly wheeling enough current to help the 75 hp to start without tripping the 255 amp breaker.
But this also shows the problem with the magnetic setting, since both motors are being fed from there own 100 amp breaker and these 100 amp breakers are not tripping, it is clearly saying that the magnetic pickup setting for the 225 amp main is set too low. requiring to have to start one motor over another might be a work around but I don't see it as a fix when most likely these two motors are operated independently, so with that in mind and the fact if the 60 hp were to ever fail they wouldn't be able to use the 75 hp then the true fix would be to reset the magnetic setting to a higher point to eliminate the tripping.
But this also shows the problem with the magnetic setting, since both motors are being fed from there own 100 amp breaker and these 100 amp breakers are not tripping, it is clearly saying that the magnetic pickup setting for the 225 amp main is set too low. requiring to have to start one motor over another might be a work around but I don't see it as a fix when most likely these two motors are operated independently, so with that in mind and the fact if the 60 hp were to ever fail they wouldn't be able to use the 75 hp then the true fix would be to reset the magnetic setting to a higher point to eliminate the tripping.