petersonra
- Northern illinois
- Semi-retired engineer
that is not my understanding from long chats with the product managers that market these things.
there is often a minimum size enclosure specified as part of the instructions.
I have seen a few that the instructions mention it is for ul508a applications, so they could only be assembled into a UL508a listed panel. But not all of them say that.
if what you are saying is true, only an enclosed starter with the label on it would be over 5kA.
by the way, kaic is a rating for the interrupting device such as the CB or fuse. the assembly has a short circuit current rating measured in kA. There is a big difference.
Are you also saying that the charts supplied by UL listing the parts that can be assembled together to form an assembly with a specified SCCR are incorrect in some way?
Here is a typical chart from UL. Are you saying this cannot be used? I have charts like this made by UL for all kinds of combinations of parts.
View attachment 3RW SCCR ratings Rec 12_19_12.pdf