3-11 Log #2229 NEC-P03 Final Action: Reject
(300.3(B)(1) Exception)
____________________________________________________________
Submitter: Donald A. Ganiere, Ottawa, IL
Recommendation: Delete the following:
Exception: Conductors installed in nonmetallic raceways run underground
shall be permitted to be arranged as isolated phase installations. The raceways
shall be installed in close proximity, and the conductors shall comply with the
provisions of 300.20(B).
Substantiation: The exception is not required. Such installations are permitted
by 300.3(B)(3) in all locations, not just underground locations.
Panel Meeting Action: Reject
Panel Statement: This exception is necessary to permit installations where
nonmetallic raceways are installed in close proximity with all of Phase A in one
raceway, all of Phase B in another raceway, all of Phase C in another, and all
the grounded conductors in another raceway. Where this is useful is between
underground manholes so the phase conductors can exit the raceways and be
easily racked within the manhole, taking up less space, and making it easier to
do testing and maintenance on the installation. This would not be permissible
without this exception.
Number Eligible to Vote: 13
Ballot Results: Affirmative: 13
 