Minimum Size Grounded Conductor for a Branch Circuit

Status
Not open for further replies.

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Smart I think you make a very good point, however, I would be curious if the intent was to mean the grounded conductor to be smaller. Good find.

Personally I think there should be a statement in 210.19 that states the grounded conductor for a branch circuit shall never be smaller than the egc. That would be consistent with the rest of the code and, I believe, that is the intent.
 

Smart $

Esteemed Member
Location
Ohio
Smart I think you make a very good point, however, I would be curious if the intent was to mean the grounded conductor to be smaller. Good find.

Personally I think there should be a statement in 210.19 that states the grounded conductor for a branch circuit shall never be smaller than the egc. That would be consistent with the rest of the code and, I believe, that is the intent.
I agree, and doubt the intent was to permit a circuit conductor to be smaller than its EGC. I believe the possibility has simply been overlooked due to other requirements keeping the probability of such extremely low.
 

kbsparky

Senior Member
Location
Delmarva, USA
I've connected several hot tubs with a reduced neutral. They required a 50 Amp circuit, but the neutral was only for the control wiring and a light. All the main loads operated on 240 Volts.

So, we installed #6 hots, a #10 neutral, and a #10 ground. :D

FWIW, the internal neutral wire was only a #14 coming from the terminal block.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I've connected several hot tubs with a reduced neutral. They required a 50 Amp circuit, but the neutral was only for the control wiring and a light. All the main loads operated on 240 Volts.

So, we installed #6 hots, a #10 neutral, and a #10 ground. :D

FWIW, the internal neutral wire was only a #14 coming from the terminal block.
Yeah but what goes on inside the tub is not our issues. I have seen reduced neutrals also but they have never been smaller then the EGC.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
but the neutral was only for the control wiring and a light. All the main loads operated on 240 Volts.

Exactly, the load for the neutral could have been a #12 but they probably realized it was a bad idea to have the neutral smaller than the egc.
 