Well there's more than that in 334.12... so are you saying the building is not of a Type III, IV, or V construction? If yes, then you can't use it.


But if it is type III, can NM-B still be used? Or does the feed count as "service entrance"?
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
If Type III construction, and there are no other prohibiting conditions, yes it can be used. A feeder is what it is.


So unless exterior run, inside it is a feeder so if cost comes nocking in the bid I could pull 6/3 NM-B or 6/3 MC from the electrical room up to the subpanel.

Very good then :D


Ok, one more question. :angel: If the electrical room is none accessible to tenants (locked door to authorized personnel only), would the subpanel need a main breaker or is main lug good?
 

Smart $

Esteemed Member
Location
Ohio
... If the electrical room is none accessible to tenants (locked door to authorized personnel only), would the subpanel need a main breaker or is main lug good?
See 240.24(B)(2). In short, MLO if there is 24/7 continuous building management supervision. Otherwise MCB or unlocked electrical room door.
 