Senior Member
- Location
- 2 Phase Philly
I have a 3ph panel from which I have to power 3 1ph machines, a mill, a lathe, and a fan. They are 9A, 7A, and 8A respectively and here's what I think my options are, check my sanity and tell me what you think:
(9Ax1.25)+8+7=26.25A
A 30A 2W circuit with #10 feeders and #14 taps to 30A recpts, put 30A plugs on the equipment in place of their 15A plugs. Any violation?
A 30A 2w circuit with #10 feeders and #14 taps to 15A recpts protected by some sort of ocp. I've seen jbox plates with a switch and a fuse but that's 120V only. Any products out there short of a full size disconnect?
A 20A 3w circuit with #12 feeders and #14 taps to 15A recpts. (9Ax1.25)+8=19.25A
A 30A 2W feeder to a subpanel near the machines with 15A breakers to feed machines. More $
3 separate 15A circuits. This will create conduit/box/panel fill issues that can only be resolve with more conduit and a subpanel at the main...not an option, $$$$
Thanks.
(9Ax1.25)+8+7=26.25A
A 30A 2W circuit with #10 feeders and #14 taps to 30A recpts, put 30A plugs on the equipment in place of their 15A plugs. Any violation?
A 30A 2w circuit with #10 feeders and #14 taps to 15A recpts protected by some sort of ocp. I've seen jbox plates with a switch and a fuse but that's 120V only. Any products out there short of a full size disconnect?
A 20A 3w circuit with #12 feeders and #14 taps to 15A recpts. (9Ax1.25)+8=19.25A
A 30A 2W feeder to a subpanel near the machines with 15A breakers to feed machines. More $
3 separate 15A circuits. This will create conduit/box/panel fill issues that can only be resolve with more conduit and a subpanel at the main...not an option, $$$$
Thanks.