DansProfElec
Member
- Location
- Huntington beach, CA
I am bidding a job to run 13 tenant store front signs (LED signs, load is .53 - .78 Amp each) that were originally run from the tenant's sub panel. The management company wants all the signs on one control and run off the house panel. I will need to run conduit and wire from a contactor control panel to areas above all 13 suites which have a small attic space above the suites. The sign company already installed the signs to j-boxs in the T-bar ceiling and put an on/off switch in the knockout hole for each sign. The sign company ran a 5 foot piece of 12/2 MX/BX cable from sign j-box mounted just above the T-bar through the 1/2" plywood ceiling into the attic area to a j-box in the attic.
NEC says each tenant gets one 20 A circuit with no other loads but the sign(s). I read that you can install more than one sign per tenant as long as the total sign load is less than 16A. If I'm rating the conductors for the runs to determine conductor size (using the voltage drop calculator) Do I use the 16A max load or the real max load which is 1.7A? Is there a poble with the 5 foot MX/BX cable being a 12/2 if I run a #8 to the farthest run?
House panel is 200A 3 Phase 120/208 with 11 open spaces. The house panel is located about 20 feet from the corner of the northeast corner of the building. Farthest run from the house panel is over 378 feet. Closest run is 70 feet.
Instead of running EMT all over the roof, I was considering installing a new subpanel and contactor control panel in the attic area above the suites at the halfway point and running the signs off of the new sub. Is there a problem with having an installation like that?
This is the first time I have bid a job like that, all other commercial properties run the power of the tenants sub.
If anyone has any better ideas I am all ears.
Thanks
Dan
NEC says each tenant gets one 20 A circuit with no other loads but the sign(s). I read that you can install more than one sign per tenant as long as the total sign load is less than 16A. If I'm rating the conductors for the runs to determine conductor size (using the voltage drop calculator) Do I use the 16A max load or the real max load which is 1.7A? Is there a poble with the 5 foot MX/BX cable being a 12/2 if I run a #8 to the farthest run?
House panel is 200A 3 Phase 120/208 with 11 open spaces. The house panel is located about 20 feet from the corner of the northeast corner of the building. Farthest run from the house panel is over 378 feet. Closest run is 70 feet.
Instead of running EMT all over the roof, I was considering installing a new subpanel and contactor control panel in the attic area above the suites at the halfway point and running the signs off of the new sub. Is there a problem with having an installation like that?
This is the first time I have bid a job like that, all other commercial properties run the power of the tenants sub.
If anyone has any better ideas I am all ears.
Thanks
Dan