Ive never used mwbc. Never trained that way. So im wondering if its to code and practicle to run 2 t8 bc with 15amp each on a shared neutral? 3 phase 120v. Thanks in advance!
So im wondering if its to code and practicle to run 2 t8 bc with 15amp each on a shared neutral?
Totally up to you.
I did an 1100' long dairy barn using MWBC's because of the wire savings as well as it helped with voltage drop.
Ask yourself, what'll happen if the breaker trips? Is everyone going to be in the dark now because you tripped TWO circuits instead of just one? Or is that even an issue? MWBC's are almost nonexistant with new installs are shop does with the recent code rules.
Ive never used mwbc. Never trained that way. So im wondering if its to code and practicle to run 2 t8 bc with 15amp each on a shared neutral? 3 phase 120v. Thanks in advance!
Wait, is this a dwelling? Then consider 210.12 as well.