I don't know the source of the document, but it appears to be unfamiliar with Section 502.5. Now if it were titled "Hazardous (Classified) Location Classifications" it would be relatively accurate.
I may not be aware that there are different set of Classes, Divisions, And groups classifications for the NEC other than the ones that I had posted.
I was to understand that one needs to first identify the classification of the area that the enclosure is to be located in first and then source an enclosure that is listed for that area and installed as directed per the NEC but I may be mistaken.
Class II Locations: Are those which are hazardous due to the presence of combustible dust.
Division I Locations in which hazardous concentrations in the air exist continuously, intermittently, or periodically under normal operating conditions.
Division II Locations in which hazardous concentrations are handled, processed, or used but are normally within closed containers or closed systems from which they can escape only in case of accidental rupture or breakdown.