When calculating the neutral on a single phase feeder do we calculate the neutral on a continuous lighting load as continuous(125%) or calculate the neutral at 100% of the lighting demand?
When calculating the neutral on a single phase feeder do we calculate the neutral on a continuous lighting load as continuous(125%) or calculate the neutral at 100% of the lighting demand?
215.2(A)(1) Exception No. 2 permits feeder grounded conductors not connected to any OCPD to be sized at 100 percent of the continuous and noncontinuous load.