Non Insulated Connector

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
Is using a non insualted EMT connector you would need a bushing on the end of the connector. Is that correct? Thank you......
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Even if the connectors are insulated ?
Why is it for #4 and larger and not smaller?
No, insulated throats can be used in lieu of a bushing but the title of your thread says non-insulated connector which is what I was responding to. Smaller conductors have less risk of being damaged so the bushing is not needed.
 
Top