why do you want a 20A versus a 15A OCPD?
Spare capacity and other reasons.
why do you want a 20A versus a 15A OCPD?
The definition of Branch Circuit is "The CIRCUIT CONDUCTORS between the final overcurrent device protecting the circuit and the outlet(s)."
210.20(C) sends you to 240.3 so that you don't ignore the equipment protection when sizing branch circuit OCPD. And 240.3 sends you to Art 210 so that you don't ignore the branch circuit conductor protection when sizing OCPD for equipment. I think its a CYA thing. But the equipment is not part of the branch circuit.
Ok, I see your point. I have to think about that. so, where do you then go to calculate the OCPD for a piece of equipment, if other than an appliance?
Spare capacity and other reasons.
I recently completed an upgrade to a WTP, and it's "on line" two years ago. We had 20.5kV UV (20 units). I just used the mfr's rating with a 40A service to each unit.
In your situation, 20A is OK. You're providing the required power and the 20A circuit breaker, 480V, 3PH is used to protect the feeder cable. (Just like you provide 20A, 120V, 1PH to your hardwired ceiling lights.)
Wherever 240.3 directs you. EG, Art 440 for Air conditioning, Art 630 for electric welders, Art 450 for transformers, etc.
Ok, we keep going around with this. My equipment is not a piece listed on tabe 240.3 hence where do you go from there, must it be one from the table that best fits? Then, would it indeed be an appliance as a "best fit".
OK, let me try this...You have this piece of UV disinfection equipment.
1) Is it "utliization equipment"...Yes, it uses electric energy for a specific purpose.
2) Is it built in standardized sizes and types...Yes
3) Does it perform one or more function...Yes, it disinfects.
Looks like you have an appliance.
however, the basic definition of appliance specifically excludes most industrial equipment. How do you get past that?
I think that this is a piece of equipment that just is not easily shoehorned into any of the categories listed. I think that using the guidelines for appliances makes the most sense, even if it is not actually an appliance. The only other thing that it would be is a luminaire. look closely at the definition of luminaire and then compare a typical UV disinfection system to that definition. I think luminaire is a closer fit than appliance.
The definition of appliance say "equipment, generally other than industrial..." A UV disinfection unit could be used in industrial, commercial, residential. There is nothing specifically "industrial" about this type of equipment.
I don't think "luminaire" quite fits the bill, because the equipment is not a "lighting unit," it is a "disinfection unit."
Luminaire. A complete lighting unit consisting of a light
source such as a lamp or lamps, together with the parts
designed to position the light source and connect it to the
power supply. It may also include parts to protect the light
source or the ballast or to distribute the light. A lampholder
itself is not a luminaire.
However in this case it is a piece of industrial equipment. You are trying to parse words to make your argument, when the plain language of the definition is what should be looked at first.
That sure as heck is a lot closer to a typical UV unit than the definition of appliance. keep in mind there is no definition of lighting unit that I can find in the code so the only one that makes sense is some kind of "unit" that includes lamps of some sort. For those who would argue that UV light is not light, are not UV grow lamps considered to be luminaires? The only difference with a UV disinfection system is that the light is directed into water and not air.
Are UV lights that are used for disinfection of air streams not considered luminaires as opposed to disinfection units? Besides, there is no NEC definition of disinfection unit.
In any case, I don't think it makes much difference. Size the OCPD at 125% and be done with it. I am really surprised that the unit does not have OCP built in.
That is a large UV system there. I guess you had SCC and an HSC as well? What in the code did you use to base the circuit size on for your UV banks?
How do you know the 20A circuit is ok, what code reference? This is the part I am struggling with. What in the code says how to size the OCPD if it is not a piece of equipment listed in tablke 240.3. Is it indeed an appliance after all?