Have a customer who is insisting on a 33 panel system utilizing Enphase M250's. He currently has a 200A main breaker panel with a bus rated also at 200A, allowing me 40A of PV. My 33 panel system calculates out to 41.25A continuous load. I've considered downsizing the main, but am told that my particular breaker/frame combo is no longer made. Here's my question; is there anything in the code that prevents me from sizing my OCPD at 40A instead of 45A (next higher breaker, based on continuous load calculation). The only risk I see here is that the breaker trips because I am slightly undersized based on continuous load. I also doubt that this will ever happen, given the loads in the house and the fact that I am oversizing my wires to compensate for voltage drop. Thoughts?