It is commonly stated as 5 mA because the UL standard say it must trip between 4 and 6mA.Oh, and I stand corrected, its 6ma, not 5ma!
Don
It is commonly stated as 5 mA because the UL standard say it must trip between 4 and 6mA.Oh, and I stand corrected, its 6ma, not 5ma!
George, you are starting to think like me. That was exactly the type of analogy that I might have created. In fact, I think I'll wait a year or so, until everyone forgets having seen it here, then I'll copyright it. :wink: 8)georgestolz said:So, in essence, when the load hands you 96? on the neutral, you quit loaning it money.
georgestolz said:The neutral of a circuit carries as much current as the hot conductor when a load is connected.
Imagine that you are the GFCI. Imagine that current is money. Your right hand is handing a dollar to the load in front of you, the load hides it for a second, and then returns the dollar back into your left hand. As you keep handing the load money, you're watching how much you're giving it, because you want it back.
So, in essence, when the load hands you 96? on the neutral, you quit loaning it money.
So, when the 4mA is lost between giving current out and getting it back, the GFCI trips. The grounding conductor had nothing to do with the transaction.
Hope that weird analogy helped, somehow.
charlie b said:OK. I think the original question has been answered, so I don't feel bad about hijacking the thread. I want to ask a related question.
When my electrical contractor had finished the job, we had a discussion about GFCI receptacles and breakers. He said (much to my surprise) that if you take a wire, and short a GFCI receptacle's neutral and ground, the GFCI will trip. This is with no load on the circuit, nothing plugged into that outlet. I disagreed, since without a current-carrying load, there would be no difference in current for the GFCI electronics to sense, and therefore nothing to cause a trip.
So he did a test. He held a bare section of wire with insulated pliers, inserted the wire into the slots for neutral and ground, and sure enough the GFCI tripped. Can anyone explain why? I can only make a vague guess.
Grounded neutral. In a situation where the load side neutral is grounded and a ground fault also occurs, a parallel path through the GFCI for the ground fault current could exist. The portion of the ground fault current returning on the neutral conductor will not be sensed as differential current. This has the effect of desensitizing the GFCI. Therefore, the UL standard requires that GFCIs trip with a 6mA ground fault even when the neutral and ground are connected. To meet this requirement, GFCIs trip when the load side neutral and equipment grounding conductors are joined, even if there is no ground fault.
aftershock said:I never understood how a GFCI could detect a ground fault if there is no ground.
sparky_magoo said:The GFCI can't detect a ground fault. .
180, actually.sparky_magoo said:The current on the hot & neutral are 90 degrees out of phase and will cancel each other out.
The latter, which could be said to indicate the former.sparky_magoo said:Is it actually detecting a ground fault or an imbalance in the current between the two conductors?
sparky_magoo said:Is it actually detecting a ground fault or an imbalance in the current between the two conductors?