125% continuous plus non-continuous rule would not be applied in the case of a residence as the examples in the back of the code show. As I stated in another thread the reasoning is that in a dwelling, lighting and receptacle loads are calculated together and not separately. If receptacles are non-continuous then how would you separate the continuous from the non-continuous calculated loads? Besides in most residences the service is usually 240/120 Volt single phase 3-wire. You could not apply the derating factors to these cases either.
You could apply the 125% continuous plus non-continuous rule in a store building where the lighting and receptacle loads are calculated separately as shown in annex D of the code but because that particular case is three wire the derating factors would not apply.
You could apply the 125% continuous plus non-continuous rule in a store building where the lighting and receptacle loads are calculated separately as shown in annex D of the code but because that particular case is three wire the derating factors would not apply.