How are they doing those tests?The power company here terminated thier end of a 4000 amp service not long ago and cut off more than one of their 2 hole compression lugs and reterminated before they were satisfied with the resistance readings they were getting.
JAP>
In my experience large termination resistance would be basically nonexistent: Often in the teens to single microohms.