yeaah u are right, it is not up to the currents really, so how can a relay dedect the sequence?? when i draw RST and RTS i think h both of them are same arent they? no matter what names they have, even if u reverse two of them it is again three phase with 120 degree apart ??? i am confused really..
You have to keep up with your labels. The order in which they reach the positive peak will be different.
Plot the following three curves:
A=SQRT(2)*120*COS(2*Pi*60*t+0*Pi/180)
B=SQRT(2)*120*COS(2*Pi*60*t-120*Pi/180)
C=SQRT(2)*120*COS(2*Pi*60*t-240*Pi/180)
Let t vary from 0 to 1/60 in increments of 1/1200 or so. Let A be red, B be yellow, and C be blue.
The graph will show 3 sinusoidals. As you move from left to right, the first peak will be the red wave at 0 seconds, the next peak will be the yellow wave at 0.0055556 seconds, and the next will be the blue at 0.0111111 seconds. That is an ABC sequence.
Now Plot the following three curves:
C=SQRT(2)*120*COS(2*Pi*60*t-120*Pi/180)
B=SQRT(2)*120*COS(2*Pi*60*t-240*Pi/180)
Let t vary from 0 to 1/60 in increments of 1/1200 or so. Again, let A be red, B be yellow, and C be blue.
The graph will again show 3 sinusoidals. As you move from left to right, the first peak will be the red wave at 0 seconds, the next peak will be the blue wave at 0.0055556 seconds, and the next will be the yellow at 0.0111111 seconds. That is an ACB sequence.