I cannot understand how anyone could take article 440 out of context to mean that as long as you size the conductor for min ampacity, you can use the max ocpd. I called a manufacturer, and they said all circuits must have an ocpd that is correctly sized to the max ampacity of the conductor, not the min ampacity of the appliance. The code even specifies that it 440 is in addition to 240.
440.21 General. The provisions of Part III specify devices intended to protect the branch-circuit conductors, control apparatus, and motors in circuits supplying hermetic refrigerant motor-compressors against overcurrent due to short circuits and ground faults They are in addition to or amendatory of the provisions of Article 240.
You are going to cause house fires! Noone in the HVAC trade would agree with this
440.21 General. The provisions of Part III specify devices intended to protect the branch-circuit conductors, control apparatus, and motors in circuits supplying hermetic refrigerant motor-compressors against overcurrent due to short circuits and ground faults They are in addition to or amendatory of the provisions of Article 240.
You are going to cause house fires! Noone in the HVAC trade would agree with this