So lets say hypothetically you do a service upgrade and you use a wood product that does not comply with the building code should that service pass inspection anyway?
It should pass the electrical inspection. If you drill more than 40% of an exterior wall (stud) the building inspector will fail the 'job" not the electrical inspector.
I really don?t see what the problem is, it?s not an NEC code thing it is a Building Code issue.
We are generally not at liberty to install into other possible BC violations.
By BC around here one cannot put simple non treated wood down on concrete at floor level (street level) or on sub basement floors; I don?t think it?s a stretch to say that also includes under grade walls.
I think that it is a stretch. Stretch is not in the code.
If the code is followed:
"SECTION R406 FOUNDATION WATERPROOFING AND DAMPPROOFING
R406.1 Concrete and masonry foundation dampproofing.
Except where required to be waterproofed by Section R406.2, foundation walls that retain earth and enclose habitable or usable spaces located below grade shall be dampproofed from the top of the footing to the finished grade. Masonry walls shall have not less than 3/8 inch (9.5 mm) portland cement parging applied to the exterior of the wall. The parging shall be dampproofed with a bituminous coating, 3 pounds per square yard (1.63 kg/m2) of acrylic modified cement, 1/8-inch (3.2 mm) coat of surface-bonding mortar complying with ASTM C 887 or any material permitted for waterproofing in Section R406.2. Concrete walls shall be dampproofed by applying any one of the above listed dampproofing materials or any one of the waterproofing materials listed in Section R406.2 to the exterior of the wall.
Exception: An existing foundation shall not be required to be dampproofed where a supplemental interior foundation drainage system is tied to a sump pump."
Then the plywood for your panel is no longer in a damp location.
YES they do. There is a listing and an installation requirement for just about every building material out there. You are not going to find it in the NEC because the NEC is only concerned with the materials that are directly related to electrical. This does not mean you can ignore the building codes or the requirements of the other materials. I would bet any one here who thinks other wise doesn't have a copy of the building code or any of the other standards that are referenced in it.
As to the comment on the "fasteners" there is a standard for those too.
Yes there is a listing. And as I said in my first post the plywood satisfies the code.
You could go to
www.apawood.org look for TB-203. You must register to read it.