You will have a problem if you don't guy it. You can probably do it with a pair of 35 foot, class 5 poles (you will need the class 5 poles for the transverse loading in a heavy loading district like Indiana), 8M guys installed with a 1:1 lead, and 15M hand anchors. Pull enough sag out of it to maintain proper clearances. I didn't do any calculations and I am not an engineer. However, this is pretty standard. Be sure to use the proper grips for the guys and the neutral. :smile: