Since we're talking a refrigeration unit, I see no problem with the #6 secondary wire OR the manufacturer's required 60amp breaker. The running amps of the unit are well within the ampacity of the #6, and the 60 amp breaker can provide the required local disconnecting means.
I see no reason to over think this.
mxslick, the transformer secondary conductors MUST be protected in accordance with 240.21(C). The #6 secondary has an ampacity of 55 amps. The 60 amp breaker will NOT protect the #6 secondary conductors per 240.21(C)(2). The #6 will be fine from the c/b to the motor, however.
Volta is correct that the primary breaker can be sized up to 250% or 90A. Of course it is not required to be that large. Since the secondary breaker is limiting the secondary current to 83%, I'd use a smaller primary feeder. Maybe a 60A primary breaker (completely arbitrary) with 3#6+#10G feeder the transformer, 3#4+#8 bj to the 60A secondary breaker, and 3#6+#10G from the breaker to the motor.