Question about bond bushing

Status
Not open for further replies.

dcspector

Senior Member
Location
Burke, Virginia
No contradiction...you can bond around the sealtight without using bonding bushings. As a matter of fact, the use of a bonding bushing would not change the requirement to bond around the sealtight. I would use a grounding sealtight connector with an external bonding jumper to bond around the sealtight. Note that this is required even if you are not using the sealtight as the EGC, if the raceway is metallic.

Thanks Don,

When I read your post it did not make sense. Now I see what you meant.
 