Receptacle screw in adapter in light socket .how can these be Legal?
I think this is what the OP is referring to:
http://ecx.images-amazon.com/images/I/41mYalG0knL._SY300_.jpg
Receptacle screw in adapter in light socket .how can these be Legal?
Legal and code compliant are different.
I say no you can not use them.
406.4 General Installation Requirements.
Violate at least (A) (B) (C).
I keep one of those in the case with my circuit tracer. Easy way to adapt the tracer when you want to trace from a lampholder.
I keep one of those in the case with my circuit tracer. Easy way to adapt the tracer when you want to trace from a lampholder.
Legal and code compliant are different.
I say no you can not use them.
406.4 General Installation Requirements.
Violate at least (A) (B) (C).
I have been at a lot of trade conventions where electricians were required to install light bulbs. :angel:
Sent from my XT1080 using Tapatalk
Also take note that 406.9(A) omits adapters from the grounded pole requirement, and 406.9(B) only applies to grounding-type adapters.