flatlander
- Diamond bar, CA , Tempe AZ
I would like you all to weigh in I was recently asked if the following was compliant and or practical. I personally think it is compliant but not practical.
This is a remodel situation. Can you take the existing Range Feeder 6-3 w.ground and terminate it to a new Sub panel then feed two circuits one 40 amp to a 7.9 Kw cooktop and a 6.75 KW double oven.
I calculate as : 14.65 KW
subtract 12 KW from 14.65 = 2.650
2650 X 5% = 2782.5
8kw the min demand plus the amount over 12KW
8000 + 2782.5 = 10782.5
10782.5/ 240
44.93 amps
it looks ok but i feel it is impractical as this home owner entertains a lot. It will be difficult to run a new circuit as this is a condo and another unit below and concrete floor.
What do any of you think.
2650 X 5% = 2782.5
10782.5/ 240
44.93 amps