Just remember that, if you ever feed a wye secondary as a primary, to leave the "neutral" floating.
 
I'm not sure of the technical reason, but I understand severe overheating can occur in the wye-connected primary.

Yup, this is what happens. Delta-Wye transformer used in reverse with a bonding jumper left installed from XO to the transformer case, fed with 2" EMT.. Ticking time bomb. Lost a utility phase, caused a large imbalance, lots of current on the raceway.....
 

Attachments

  • 20151214_133045.jpg
    20151214_133045.jpg
    19.1 KB · Views: 0

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
I'm not sure of the technical reason, but I understand severe overheating can occur in the wye-connected primary.

The technical reason is that the delta winding imposes a constraint on the line to line (phase) voltages. Traversing the closed delta in either direction must lead to a total voltage change of 0V. Looking at it another way, the phasors must form a closed triangle when set end to end.
The output of a delta source must also automatically obey that same constraint.
But the line to neutral voltages in a wye system do not have any such constraint, and since each wye voltage transforms into a corresponding side of the delta the physical reality causes circulating currents on both the wye side and the delta side until the voltage drops on both sides allow the phasor equation to be satisfied. Those currents (particularly the neutral current) can be many times the design rating of the transformer.
The worst case happens when one POCO line to neutral phase is lost on the wye primary side.
 