newinspector1
Member
- Location
- NC
I had an inspection this morning in a business that is doing a remodel to make more office space. The electrician has ran romex throughout the building and the contractor stated that they were going to have a suspended cieling. I failed the job b/c of 334.12 A(2). The electrician called and said that it is not considered exposed if it is supported against the top plate. I have not ever heard that. I think I am right, but would like to be sure.