Can romex be used in a commercial drop ceiling? I don't know what type of construction 3,4 and 5 is. I am looking at 334.10 (3).
Servicemen have an unusual propensity to hack up romex while they're above the ceiling working. It's like a moth to a flame.peter d said:However, good luck on trying to find some logic on why it's not allowed.
peter d said:No, the building type does not factor into it.
However, good luck on trying to find some logic on why it's not allowed.
e57 said:The NFPA writes our codes and they seem to have a relationship they want to maintain with fire fighters by trying to limit flame spread and in general combustable materials installed in buildings, and the toxins released when they burn. And dropped cielings are an easy place for flame and smoke to spread.... At least thats my understanding of it....
Who knows - someday they might make and require metal clad Cat-5 as well...... Or conduit....
Anyway look at 334.12(A)(1) - pretty much eliminates NM above dropped cieling in other than one and two family resi.... Like say in commercial dropped cielings...
They don't actually write the codes. The codes are written by those who submit proposals and comments along with the volunteer members of the code making panels.The NFPA writes our codes ....
e57 said:The NFPA .... seem to have a relationship they want to maintain with fire fighters by trying to limit flame spread and in general combustable materials installed in buildings, and the toxins released when they burn. And dropped cielings are an easy place for flame and smoke to spread....
http://www.nema.org/stds/fieldreps/codealerts/20060505nj.cfm4.Chapter 3 of the electrical subcode, entitled "Wiring Methods and Materials," is amended as follows:
ii. Section 334.12(A)(2) is deleted in its entirety.
Vegas - I remember I watched some show about - it might have been NOVA???? Where whole rooms spontainiously combusted - I think it was the MGM Grand???? (It apparently started when Al FMC and copper refer tubing came in contact???) Fireballs raced around and the smoke was especially toxic.... Apparently even poker chips are flame tested now because of it.....wireguru said:they do make MC cat5, RG6, etc. some jurisdictions such as clark county (Las Vegas) require EVERYTHING to be in conduit. You cant even string a plenum CAT5 above a drop ceiling