Suppose I have a cord that falls under table 400.5(A)(2) and is 75C rated with 3 conductors. According to the table 3/0 copper has a rating of 241 amps and assume we can use the next size overcurrent protective device.
My question is --Can we install a 250 amp breaker on this cord? I have been told no because of 100.14 but I don't see it.