The hypothetical transformer under discussion does not fall under NESC compliance. Please do not confuse the discussion with NESC requirements.ronaldrc said:I understood you where not talking about a utility transformer.
But the NEC treats any SDS the same way just because the transformer is in the building doesn't mean you don't have to hook it to the earth grounding electrode on that buildings electrical system.
And even if the primary and secondary grounded conductors are bonded as the NESC requires doesn't mean it is not a SDS.
Regarding NEC compliance, a primary-side solidly grounded circuit conductor connected or otherwise bonded to the X0 terminal of the hypothetical transformer or its secondary grounded conductor removes the transformer from being classified as a separately derived system. Therefore, it is not bound to the requirements for a separately derived system.
The only question that remains, which has yet to be shown by NEC standards, is if such connection is non-compliant. Can you reference an NEC requirement which establishes said connection as non-compliant?