Ser 4/0 2/0 Cable

Status
Not open for further replies.

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Dennis Alwon said:
Frogneck-- read art. 300.4(F) -- Insulated bushings-- inspector was correct.


Sorry Dennis, I have to disagree. The requirement is for raceways not SE connectors. The inspector was incorrect.
 

stickboy1375

Senior Member
Location
Litchfield, CT
Dennis Alwon said:
That is not a reducer. It looks like a chase nipple (no threads) and slips inside a pvc coupling. It is called a box adapter --- you don't need a locknut nor bushings and it gives you a lot more space in the panels. I hardly ever use a pvc connector.


The only problem with those is future removal... if you glue it anyway....
 