MO_EE,
Under the conditions you stated, the fault being right at the load side of the second breaker, isn't it very possible that the fault current would be in the instantanuous trip range of both breakers making selective coordination impossible even with a fully rated system?
Don
Under the conditions you stated, the fault being right at the load side of the second breaker, isn't it very possible that the fault current would be in the instantanuous trip range of both breakers making selective coordination impossible even with a fully rated system?
Don