Do I need a service receptacle at a gate operator at the driveway of a dwelling unit?
Thanks
Thanks
Do I need a service receptacle at a gate operator at the driveway of a dwelling unit?
I say no as I see nothing in 210 that requires it.Thanks
I say no as I see nothing in 210 that requires it.
Are you saying because 210 part III does not require a receptacle to be placed at an electrically operated gate that would in essence not require a disconnecting means for an appliance or for a motor?
I don't see anything in the OP asking about a disconnecting means:?
I say no as I see nothing in 210 that requires it.
Code or not, an outdoor receptacle near each of these openers would have been a nice touch as I find myself having to run an extension cord when doing work in the area.
Nice idea or not unless the customer requests it and is willing to pay for it I would not install one for free.