Hello,
I am designing a low voltage distribution system for an industrial facility. I have a double ended substation with 2 x 2500KVA transformers with secondary 480V. The tie breaker is normally open. But during maintenance of one of the transformers or for any reason, when decided to supply load on one transformer, the facility wants to close the tie first and open one of the main breakers.
I am afraid that it may result in double the short circuit available current at the low voltage switchgear which is close coupled to the transformers. There are MCCs fed from this double ended unit substation. In case of SC, they contribute 4 x FLA according to ANSI. MCCs are also located close to the switchgear in the same e-room
From my calculations, the short ciruit is turning around 125KA which is way higher than 65kA and higher than 100kA which most of the equipment is designed for. I was able to find LVS available for 150KA but the MCCs are capable to handle upto 100kA only. The only way I see to limit the short circuit lower than 100kA is by increasing the impedance of the transformers which may lead to unreasonable voltage drop, I have not checked this option. Are there any other ways of resolving this issue other than increasing the impedance of the transformer?
The fact that all the three breakers are closed at the same time is certain even for a few seconds. What can we do to limit the short circuit or how the system can de distributed other than resizing the transformers and make them 1500KVA etc.
Thanks for any assistance/comments/suggestions
I am designing a low voltage distribution system for an industrial facility. I have a double ended substation with 2 x 2500KVA transformers with secondary 480V. The tie breaker is normally open. But during maintenance of one of the transformers or for any reason, when decided to supply load on one transformer, the facility wants to close the tie first and open one of the main breakers.
I am afraid that it may result in double the short circuit available current at the low voltage switchgear which is close coupled to the transformers. There are MCCs fed from this double ended unit substation. In case of SC, they contribute 4 x FLA according to ANSI. MCCs are also located close to the switchgear in the same e-room
From my calculations, the short ciruit is turning around 125KA which is way higher than 65kA and higher than 100kA which most of the equipment is designed for. I was able to find LVS available for 150KA but the MCCs are capable to handle upto 100kA only. The only way I see to limit the short circuit lower than 100kA is by increasing the impedance of the transformers which may lead to unreasonable voltage drop, I have not checked this option. Are there any other ways of resolving this issue other than increasing the impedance of the transformer?
The fact that all the three breakers are closed at the same time is certain even for a few seconds. What can we do to limit the short circuit or how the system can de distributed other than resizing the transformers and make them 1500KVA etc.
Thanks for any assistance/comments/suggestions