So - how many phases?
  • 1
    Votes: 25 89.3%
  • 2
    Votes: 0 0.0%
  • Other - and I'll explain why
    Votes: 3 10.7%
  • Total voters
    28
  • Poll closed .
charlie b
Lockport, IL
Retired Electrical Engineer
I see no liquids and no gases, so I conclude that only the solid phase is represented by your sketch. For that reason, I voted for ONE. :happyyes:
Also, if you look at the voltage between any two points on the secondary, and compare it to the voltage between any two other points, and disregard any minor changes that voltage drop might inflict, you will see two wave forms that match one, and only one of the following two descriptions:
  • Both reach their positive peaks at the same time, both reach their negative peaks at the same time, and both reach their zero crossings at the same time.
  • Both reach their zero crossings at the same time, and each reach its positive peak at the same moment the other reaches its negative peak.
That makes it "single phase," in my book.
mivey
Good points.
Assume the applied primary voltage is characterized by the general function V(t)= A sin(ωt+φ0), where A, ω and φ0are constants. Apply any arbitrary set of turns ratios you desire between the primary winding and secondary taps.
We agree on what to call the device (YEA). Not sure we agree on why yet - but we seem to be getting there.
Ok, a sinusodial input on the primary.
Given that a definition of phase has not been specified, I will make the stipulation that my technically correct definition still stands. I will further stipulate that we are not considering the number of phases present in the circuit due to currents (or we could get the 30-something? that pfalcon mentioned based on a technicality). While I'm stipluating I might as well stipulate that the voltage magnitudes on the secondary are all equal for the voltages we are considering.
With that, we can have voltages with a phase of (ωt+φ0) and voltages with a phase of (ωt+φ0+180?). So, using the technically correct definition for phase and the stipulations I noted, we can have up to two phases present at any given point in time.
However, it is still called a single-phase transformer.
rbalex
Mission Viejo, CA
Professional Electrical Engineer
You need to check your understanding of stipulate. You don't get to "stipulate" anything. You can certainly offer your definition of phase to support your position. You don't get to foreclose on the definition though.
mivey
I will add stipulations as many and as often as I please.
mivey
I guess the "beef" is you don't want me to force you to agree to anything. It was intended to be a list of stipulations and you could accept or not. But my answers are not going to be binding until you adopt those stipulations.
So, rbalex:
Did you propose a different definition or did you not mean to imply that my definition was fine? After all, hearing no objection...
mivey said:
I will further stipulate that we are not considering the number of phases present in the circuit due to currents.
Did you propose that we also consider the phase of load currents?
Did your diagram intend to open up the discussion to the phase order of systems of voltages where multiple voiltage magnitudes are present?
Thanks for the lesson in legalese.
pfalcon
Indiana
As the distinction between (ωt+φ0) and (ωt+φ0+180?) is nothing more than changing your leads from, for example, BD to DB and declaring it a different phase; I can only agree to it as a "pragmatic" interpretation of phase that will generate 30+ based on where you tap and which direction you place your taps.
Smart $
Esteemed Member
Ohio
Assume the applied primary voltage is characterized by the general function V(t)= A sin(ωt+φ0), where A, ω and φ0are constants. ...
I've been trying to stay out of this part of the discussion but find I no longer can, at least for one post :blink:
Given the reference is the primary voltage, it follows that secondary voltages be measured in the same manner. You can only have secondary voltages that I highlighted red. While you can measure voltages that I highlighted blue, they are still the same voltages... only polarity inverted. There's only 15 possible voltages at any instant, not thirty. Isn't voltage defined as the potential between two points? Flopping points to do the measuring doesn't give you a second voltage. It's still the same voltage... you are just perceiving it differently. And as I said the reference is primary voltage, if you flop leads to measure the secondary voltages, you also have to flop your reference leads. So technically, your reference timing shifted a half-cycle on the primary and you end up with secondary voltages as I highlighted red... :thumbsup:
Rightly so. :slaphead:
OK, I'm done saying all I have to say on the matter. Rhetoric may continue as normal...
mivey
Just an opinion.
I did not bother to count as I suspect it is really far removed from what rbalex wants to discuss. I just used the figure pfalcon threw out there.
mivey
Any voltage reference frame is a choice, not a given.
rbalex
Mission Viejo, CA
Yes - I'm well aware of that. It's one more thing you don't do properly. What would be proper is to cite a source for your definition rather than assuming everyone agrees with it.
pfalcon
Indiana
:thumbsup:
Same situation applies to the single center tap ANB: 1 primary (240V); 2 secondary AN, NB (120V); and three BA, BN, NA (blue) appear by flopping leads without correcting reference.
rbalex
Mission Viejo, CA
Your'e not forcing me - you're trying to force everyone
Nope - I left the definition open. You can certainly use yours to support your position. Just no one has to accept it at the moment; which is basically what "stipulate" means in this context.
Nope, They're irrelevant in my opinion for the time being.
No - but if you want to chase another rabbit - start your own thread.
You're welcome.
pfalcon
Indiana
Just an opinion.
An opinion expressing that you should be consistent in how you use a reference frame.
15 red: AB, AC, AD, AE, AF, BC, BD, BE, BF, CD, CE, CF, DE, DF, EF.
15 blue: FE, FD, FC, FB, FA, ED, EC, EB, EA, DC, DB, DA, CB, CA, BA.
Smart$ pointed out that Red & Blue are simply reversals of each other. Useful but not really unique.
AF or FA depending on your preference is the secondary coil voltage. The others are created as classic voltage divider and lead reversal voltages.
But as Smart$ points out, the waveform is only different because you reversed how you measured one axis of your 2D reference frame but were inconsistent by not reversing the second axis to match.
rbalex
Mission Viejo, CA
BTW I'm trying to see if I can alter the pole to allow changing votes. Remember, I didn't ask what the transformer was, I asked "how many phases"?
Apparently wiping it out is the best I can do - I truly apologize.
Smart $
Esteemed Member
Ohio
Had me wondering there for a split second :eek:hmy:
For the record, I voted 0 initially because you didn't specify any primary input. It would still be zero if you had spec'd a DC voltage :blink:
I see the POLL changed and I revoted 1...
mivey
I did not assume everyone agreed with it. It was the definition I used to go along with my response. My improper use of the word stipulation did not reflect my intent.
mivey
Sticking with (NOT stipulating :D) my previous definition of phase, and other clarifications, including that I am considering the secondary voltages and that voltage is a relative measurement:
Using one of the reference frame options: one.
Using a different one of the reference frame options: two
I also favor charlie b's answer because the term "phase" has not been defined by the OP so the question is really too open-ended.