gar
Senior Member
- Location
- Ann Arbor, Michigan
- Occupation
- EE
120703-1922 EDT
We are about 4.5" short on rainfall this year. Have had very few storms, and even many fewer with lightning. We are presently running hot weather, daytime usually into the 90s over the last week.
Under normal conditions the three phase voltage at my son's shop is about 240 V +/-2 V on all three phases. This is a two transformer Y primary and open delta on the secondary with a wild leg. Means one large transformer with a center tap to provide 240/120.
Last week in the middle of the day a fire occurred in the substation completely destroying it.
A number of hours later power was re-established.
A day or so later my son noticed that the 120 circuit was running about 110 V. Now it is more in the 107 to 108 range and UPSs click on and off.
I had him check the 3 phase voltages. These were about 240, 236, and 220. Called Edison over the weekend and they finally arrived today. Today is when my son learned that the substation was completely destroyed, and that a patch was made into another substation about 1 mile away. It is going to take about 13 weeks to replace the burned out sub.
The Edison servicemen agreed there was a problem and they have to get power quality out to look for and find the problem. I suspect the servicemen checked the voltage at the sub now supplying power.
Two strange items.
In the past we have been told that the substation had more capacity than necessary for its load, and prior problems we had were likely the line from the substation. It turned out that out our prior real problem was aluminum wires terminating at the transformer secondaries were arcing.
Second, in a system as large as Edison why don't they have spares for the substation? About 2,000,000 customers and many very large industrial customers.
Other information gleaned from the servicemen. They do not like the new smart meters being installed. Apparently many problems. They opened one and found what was described as a small solenoid. My guess this relates to the disconnect contactor. Another comment was that it looked cheaply made.
How do you pack a quality contactor into a package the size of an old meter and have it work reliably with a 200 A rating?. It could be this is mechanically latched and that could account for a small solenoid size. This may also relate to reports of fires in these meters.
.
We are about 4.5" short on rainfall this year. Have had very few storms, and even many fewer with lightning. We are presently running hot weather, daytime usually into the 90s over the last week.
Under normal conditions the three phase voltage at my son's shop is about 240 V +/-2 V on all three phases. This is a two transformer Y primary and open delta on the secondary with a wild leg. Means one large transformer with a center tap to provide 240/120.
Last week in the middle of the day a fire occurred in the substation completely destroying it.
A number of hours later power was re-established.
A day or so later my son noticed that the 120 circuit was running about 110 V. Now it is more in the 107 to 108 range and UPSs click on and off.
I had him check the 3 phase voltages. These were about 240, 236, and 220. Called Edison over the weekend and they finally arrived today. Today is when my son learned that the substation was completely destroyed, and that a patch was made into another substation about 1 mile away. It is going to take about 13 weeks to replace the burned out sub.
The Edison servicemen agreed there was a problem and they have to get power quality out to look for and find the problem. I suspect the servicemen checked the voltage at the sub now supplying power.
Two strange items.
In the past we have been told that the substation had more capacity than necessary for its load, and prior problems we had were likely the line from the substation. It turned out that out our prior real problem was aluminum wires terminating at the transformer secondaries were arcing.
Second, in a system as large as Edison why don't they have spares for the substation? About 2,000,000 customers and many very large industrial customers.
Other information gleaned from the servicemen. They do not like the new smart meters being installed. Apparently many problems. They opened one and found what was described as a small solenoid. My guess this relates to the disconnect contactor. Another comment was that it looked cheaply made.
How do you pack a quality contactor into a package the size of an old meter and have it work reliably with a 200 A rating?. It could be this is mechanically latched and that could account for a small solenoid size. This may also relate to reports of fires in these meters.
.