I am experiencing a strange problem with some new 350 MCM cables that are being used as a temporary source of power at a remediation site. The power source is 2000 kW, variable voltage 110 to 800, 3 phase, no ground (delta) transformer bank. The cables are the same length, copper construction. They are triple runs per phase, and each triple run feeds a copper bus-bar in the field, where loads are connected. The cables from each phase cross cables from other phases, run parallel to each other, run parallel to opposite phases, etc. as they are run to the field, and they are run across the open ground. The total length is about 240 feet. 2/0 cables feed loads from the field busbars.
Baseline Condition: 3, 350 MCM into box, 2, 2/0 out of box. Currents:
Y9 = 115 amps C2 = 175 amps
Y9A = 508 amps D1 = 155 amps
Y10 = 637 amps
Change 1: Remove all 2/0 from box. Therefore 3, 350 MCM into box, 0, 2/0 out of box. Currents:
Y9 = 200 amps
Y9A = 470 amps
Y10 = 570 amps
Change 2: Remove 1, 350 cable. Therefore, 2, 350 MCM into box, 0, 2/0 out of box. Currents:
Y9 = 214 amps
Y9A = 217 amps
Change 3: Install 2 2/0 loads. Therefore, 2, 350 MCM into box, 2, 2/0 out of box. Currents:
Y9 = 216 amps C2 = 166 amps
Y9A = 306 amps D1 = 146 amps
Change 4: Install 2 more 2/0 loads. Therefore, 2 350 MCM into box, 4, 2/0 out of box. Currents:
Y9 = 309 amps C2 = 160 amps
Y9A = 434 amps D1 = 139 amps
G4 = 131 amps
E3 = 195 amps
So why do we have a total 1240 amps measured on the 350 MCMs with no loads hooked up to them? Why, in change 2, are the amperage readings just about equal, (214 amps) when there is supposedly no load on them? Can an inductive load be imposed on cables of the opposite phase under heavy resistive load, when in close proximity to each other. How about on cables of the same phase? How about under no-load conditions?
Baseline Condition: 3, 350 MCM into box, 2, 2/0 out of box. Currents:
Y9 = 115 amps C2 = 175 amps
Y9A = 508 amps D1 = 155 amps
Y10 = 637 amps
Change 1: Remove all 2/0 from box. Therefore 3, 350 MCM into box, 0, 2/0 out of box. Currents:
Y9 = 200 amps
Y9A = 470 amps
Y10 = 570 amps
Change 2: Remove 1, 350 cable. Therefore, 2, 350 MCM into box, 0, 2/0 out of box. Currents:
Y9 = 214 amps
Y9A = 217 amps
Change 3: Install 2 2/0 loads. Therefore, 2, 350 MCM into box, 2, 2/0 out of box. Currents:
Y9 = 216 amps C2 = 166 amps
Y9A = 306 amps D1 = 146 amps
Change 4: Install 2 more 2/0 loads. Therefore, 2 350 MCM into box, 4, 2/0 out of box. Currents:
Y9 = 309 amps C2 = 160 amps
Y9A = 434 amps D1 = 139 amps
G4 = 131 amps
E3 = 195 amps
So why do we have a total 1240 amps measured on the 350 MCMs with no loads hooked up to them? Why, in change 2, are the amperage readings just about equal, (214 amps) when there is supposedly no load on them? Can an inductive load be imposed on cables of the opposite phase under heavy resistive load, when in close proximity to each other. How about on cables of the same phase? How about under no-load conditions?