He may be referring to Table 310.15(B)(6)
He may be referring to Table 310.15(B)(6)
I just want to know what size wire to use for 125 amp panel.
I dont have a set of plans.
It is 120/240 volt.
why is it not the same on 3 phase 120/208?
the main is 125 amp single phase for each apt. why would it be 2/0 on 120/208 and 1/0 alu on 120/240?
If the service voltage is 120/240 you could use 1/0 AL per Table 310.15(B)(6)