I have the following issues during the inspection of a480Y/277VAC, 4000A MDP. Where in the code does it say these are violations?
1. Conductors crushed/lying on uninsulated parts of MDP framing.
2. Conductors have sizable nicks/cuts from pulling in.
3. Conductors (insulated) laying against MDP bus work.
4. Conductors not supported exiting conduits to breakers.
5. 450A rated and 600A rated panelboard have 800A MCB's installed.
As usual, thanks for any and all responses.
1. Conductors crushed/lying on uninsulated parts of MDP framing.
2. Conductors have sizable nicks/cuts from pulling in.
3. Conductors (insulated) laying against MDP bus work.
4. Conductors not supported exiting conduits to breakers.
5. 450A rated and 600A rated panelboard have 800A MCB's installed.
As usual, thanks for any and all responses.